Modius Data Center Blog

Measuring PUE with Shared Resources, Part 2 of 2

Posted by Jay Hartley, PhD on Wed, May 25, 2011 @ 05:02 PM

PUE in an Imperfect World

Last week I started discussing the instrumentation and measurement of PUE when the data center shares resources with other facilities. The most common shared resource is chilled water, such as from a common campus or building mechanical yard. We looked at the simple way to allocate a portion of the power consumed by the mechanical equipment to the overall power consumed by the data center.

The approach there assumed perfect sub-metering of both the power and chilled water, for both the data center and the mechanical yard. Lovely situation if you have it or can afford to quickly achieve it, but not terribly common out in the hard, cold (but not always cold enough for servers) world. Thus, we must turn to estimates and approximations.

Of course, any approximations made will degrade the ability to compare PUEs across facilities--already a tricky task. The primary goal is to provide a metric to measure improvement. Here are a few scenarios that fall short of the ideal, but will give you something to work with:

  • Calculate PUE pPUECan’t measure data-center heat load, but have good electrical sub-metering. Use electrical power as a substitute for cooling load. Every watt going in ends up as heat, and there usually aren’t too many people in the space routinely. Works best if you’re also measuring the power to all other non-data-center cooled space. The ratio of the two will get you close to the ratio of their cooling loads. If there are people in a space routinely, add 1 kWh of load per head per 8-hr day of light office work.
  • Water temperature is easy, but can’t install a flow meter. Many CRAHs control their cooling power through a variable valve. Reported “Cooling Load” is actually the percentage opening of the valve. Get the valve characteristics curve from the manufacturer. Your monitoring system can then convert the cooling load to an estimated flow. Add up the flows from all CRAHs to get the total.
  • Have the head loads, but don’t know the mechanical yard’s electrical power. Use a clamp-on hand meter to take some spot measurements. From this you can calculate a Coefficient of Performance (COP) for the mechanical yard, i.e., the power consumed per cooling power delivered. Try to measure it at a couple of different load levels, as the real COP will depend on the % load.
  • I’ve got no information about the mechanical yard. Not true. The control system knows the overall load on the mechanical yard. It knows which pumps are on, how many compressor stages are operating, and whether the cooling-tower fan is running. If you have variable-speed drives, it knows what speed they’re running. You should be able to get from the manufacturer at least a nominal COP curve for the tower and chiller and nominal power curves for pumps and fans. Somebody had all these numbers when they designed the system, after all.

Whatever number you come up with, perform a sanity check against the DOE’s DCPro online tool. Are you in the ballpark? Heads up, DCPro will ask you many questions about your facility that you may or may not be prepared to answer. For that reason alone, it’s an excellent exercise.

It’s interesting to note that even the Perfect World of absolute instrumentation can expose some unexpected inter-dependencies. Since the efficiency of the mechanical yard depends on its overall load level, the value of the data-center PUE can be affected by the load level in the rest of the facility. During off hours, when the overall load drops in the office space, the data center will have a larger share of the chilled-water resource. The chiller and/or cooling-tower efficiency will decline at the same time. The resulting increase in instantaneous data center PUE does not reflect a sudden problem in the data center’s operations; though it might suggest overall efficiency improvements in the control strategy.

PUE is a very simple metric, just a ratio of two power measurements, but depending on your specific facility configuration and level of instrumentation, it can be remarkably tricky to “get it right.” Thus, the ever-expanding array of tier levels and partial alternative measurements. Relatively small incremental investments can steadily improve the quality of your estimates. When reporting to management, don’t hide the fact that you are providing an estimated value. You’ll only buy yourself more grief later when the reported PUE changes significantly due to an improvement in the calculation itself, instead of any real operational changes.

The trade-off in coming to a reasonable overall PUE is between investing in instrumentation and investing in a bit of research about your equipment and the associated estimation calculations. In either case, studying the resulting number as it varies over the hours, days, and seasons can provide excellent insight into the operational behavior of your data center.

Topics: BMS, Dr-Jay, PUE, instrumentation, Measurements-Metrics, pPUE

Measuring PUE with Shared Resources, Part 1 of 2

Posted by Jay Hartley, PhD on Wed, May 18, 2011 @ 09:02 AM

Last week I wrote a little about measuring the total power in a data center, when all facility infrastructure are dedicated to supporting the data center. Another common situation is a data center in a mixed environment, such as a corporate campus or an office tower, at which the facility resources are shared. The most common shared resource is the chilled-water system, often referred to as the “mechanical yard.” As difficult as it sometimes can be to set up continuous power monitoring for a stand-alone data center, it is considerably trickier when the mechanical yard is shared. Again, simple in principle, but often surprisingly painful in practice.

Mixed Use Facility

One way to address this problem is to use The Green Grid’s partial PUE, or pPUE. While the number should not be used as a comparison against other data centers, it provides a metric to use for tracking improvements within the data center.

This isn’t always a satisfactory approach, however. Given that there is a mechanical yard, it’s pretty much guaranteed to be a major component of the overall non-IT power overhead. Using a partial PUE (pPUE) of the remaining system and not measuring, or at least estimating, the mechanical yard’s contribution masks both the overall impact of the data center and the impact of any efficiency improvements you make.

There are a number of ways to incorporate the mechanical yard in the PUE calculations. Full instrumentation is always nice to have, but most of us have to fall back on approximations. Fundamentally, you want to know how much energy the mechanical yard consumes and what portion of the cooling load is allocated to the data center.

Data Center Mechanical Plant

The Perfect World

In an ideal situation, you have the mechanical yard’s power continuously sub-metered—chillers, cooling towers, and all associated pumps and fans. Not unusual to have a single distribution point where measurement can be made. Perhaps even a dedicated ATS. Then for the ideal solution, all you need is sub-metering of the chilled-water going into the data center.

The heat load, h, of any fluid cooling system can be calculated from the temperature change, ∆T, and the overall flow rate, qh=Cq∆T, where C is a constant that depends on the type of fluid and the units used. As much as I dislike non-metric units, it is easy to remember that C=500 when temperature is in °F and flow rate is in gal/min, giving heat load in BTU/h. (Please don’t tell my physics instructors I used BTUs in public.) Regardless of units, the total power to allocate to your data center overhead is Pdc=Pmech (hdc⁄hmech). Since what matters is the ratio, the constant C cancels out and you have Pdc=Pmech (q∆Tdcq∆Tmech ).

You’re pretty much guaranteed to have the overall temperature and flow data for the main chilled-water loop in the BMS system already, so you have q∆Tmech. Much less likely to have the same data for just the pipes going in and out of your data center. If you do, hurrah, you’re in The Perfect World, and you’re probably already monitoring your full PUE and didn’t need to read this article at all.

Perfect and You Don’t Even Know It

Don’t forget to check the information from your floor-level cooling equipment as well. Some of them do measure and report their own chilled-water statistics, in which case no additional instrumentation is needed. In the interest of brand neutrality, I won’t go into specific names and models in this article, but feel free to contact me with questions about the information available from different equipment.

Perfect Retrofit

If you’re not already sub-metered, but you have access to a straight stretch of pipe at least a couple feet long, then consider installing an ultrasonic flow meter. You’ll need to strap a transmitter and a receiver to the pipe, under the insulation, typically at least a foot apart along the pipe. No need to stop the flow or interrupt operation in any way. Either inflow or outflow is fine. If they’re not the same, get a mop; you have other more pressing problems. Focus on leak detection, not energy monitoring.

If the pipe is metal, then place surface temperature sensors directly on the outside of the inflow and outflow pipes, and insulate them well from the outside air. Might not be the exact same temperature as the water, but you can get very close, and you’re really most concerned about the temperature difference anyway. For non-metal pipes, you will have to insert probes into the water flow. You might have available access ports, if you’re lucky.

The Rest of Us

Next week I’ll discuss some of the options available for the large population of data centers that don’t have perfect instrumentation, and can’t afford the time and/or money to purchase and install it right now.

Topics: BMS, Dr-Jay, PUE, instrumentation, Measurements-Metrics, pPUE

Monitoring Total Energy for PUE

Posted by Jay Hartley, PhD on Mon, May 09, 2011 @ 02:34 PM

I am routinely surprised at how difficult it can be to determine the total energy consumption for many data centers. Stand-alone data centers can at least look at the monthly bill from the utility, but as the Green Grid points out when discussing PUE metrics, continuous monitoring is preferred whenever possible. Measurement in an environment where resources, such as chilled water, are shared with non-data center facilities can be even more complex. I’ll discuss that topic in the coming weeks. For now, I want to look just at the stand-alone data center.

PUE, Dashboard, Monitoring

In general, the choices are pretty simple for a green-field installation. The only real requirement is commitment to buying the instrumentation. Solid-core CTs are cheaper, and generally smaller for the same current range. Wiring in the voltage is easy. Retrofits are more interesting. Nobody likes to work on a hot electrical system, but shutting down a main power feed is a risky process, even with redundant systems.

One logical metering point is the output of the main transfer switches. Many folk assume they already have power metering on their ATS. It has an LCD panel showing various electrical readings, after all. Unfortunately, more often than not, only voltage is measured. That’s all the switch needs to do its job. Seems that the advanced metering option is either overlooked or the first thing to go when trimming the budget.

Retrofitting the advanced option into an ATS is not trivial. Clamping on a few CTs might not seem tough, but the metering module itself generally has to be completely swapped out. Full shut-down time.

A separate revenue-grade power meter is not terribly expensive these days. In some cases it may even be competitive with the advanced metering option from your ATS manufacturer. Meters that include power-quality metrics such as THD can be found for less than $3K, CTs included. Such a meter could be installed directly on the output of the ATS, but the input of the main distribution panel is generally a better option.

Clamping on the CTs is relatively straightforward, even on a live system, though it can be tricky if the cabling is wired too tightly. Slim, flexible Rogowski coils are an excellent option in this case. A bit pricier, but ease of installation can make back the difference in labor pretty quickly.

For voltage sensing, distribution panels often have spare output terminals available. This is ideal in a retrofit situation, and desirable even in a new install. Odds are the breaker rating is higher than the meter could handle, so don’t forget to include protection fusing. If no spare circuit is available, you can perhaps find one that is at least non-critical, such as a lighting circuit, and could be shut down long enough to tie in the voltage.

Worst-case retrofit scenario, you have no local voltage connections available. CTs alone are better than nothing. A good monitoring system can combine those readings with nominal voltages, or voltages from the ATS, to provide at least apparent power. Most meters can be powered from a single-phase voltage supply, even 110V wall power. I recommend springing for the full power meter even in this case. At some point you’ll likely have some down time, hopefully scheduled, on this circuit, and you can perform the full proper wiring at that time.

The final decision about your meter is whether to get the display. If your goal is continuous measurement (i.e., monitoring), the meter should be communicating with a monitoring system. The LED or LCD display will at best provide you a secondary check on the readings. The option also complicates the installation, because you need some kind of panel mounting to hold it and make it visible. It can become more of a space issue than one might expect for a 25-sq. inch display. Avoiding the full display output saves on the cost of the meter, and saves even more on the installation labor.

Look for a meter with simple LEDs or some other indicator to help identify wiring problems like mis-matched current and voltage phases. If the meter is a transducer only, have the monitoring system up and running, and communication wiring run, before installing the meter, so you can use its readings to troubleshoot the wiring. Nobody wants to open that panel twice!

Continuous monitoring of total power is critical to managing the capacity and efficiency of a data center. Whether your concern is PUE, carbon footprint, or simply reducing the energy bill, the monthly report from the utility won’t always provide the information you need to identify specific opportunities for improvement. Even smart meters might not be granular enough to identify short-term surges, and won’t allow you to correlate the data with that from other equipment in your facility. It’s hard to justify skimping on one or two meters for a new data center. Even in a retrofit situation, consider a dedicated meter as an early step in your efficiency efforts.

Topics: Energy Efficiency, Dr-Jay, PUE, data center energy monitoring, monitoring